Header for window at top of foundation wall?
Hi, this is my first post here. I am designing an accessory dwelling unit using FreeCAD. Very interesting and challenging process. I am using a post and beam scheme where 4x4 posts support the entire upper floor load, so that the rest of the framing only has to support itself. As such I should not need much in the way of headers and cripples.
My question is about the window cutouts in the foundation wall. Normally, you have a structural steel header at the top of each opening in a concrete wall, but here there is essentially no load above these windows. In the model, I just have the sill plate and bottom plate spanning the opening:

I am obsessing over how much I need to beef this up, if at all. I would like to use as much as the window opening as possible for window and not have any big header if I can avoid it. Does this work? And does my fairly arcane DIY construction question belong here in this forum?
(edit) OK, I need a header there, but not much of one I think, given that it's not load bearing. Revised model with 2x4 header with jack studs:

This this there will be a solid 6 inches of wood above the window tops: 2x4 header, sillplate, subfloor, bottom plate. Overkill, probably.
The door isn't right yet. It needs special treatment because a ventilation duct has to enter the basement there.
(edit2) Main floor view showing the floor system, using lvl 2x4 joists sitting on angle iron beams:

As it turned out, the structural steel beams in this image are not strong enough. Something about the inverse cubic relationship between beam depth and deflection. I was able to learn enough basics of beam calculations to design beams that are stiff enough, but haven't modeled them yet. Some of the main floor beams will be more than four inches deep, but only one actually intrudes into the living space. I will try to make that look intentional by putting pot lights in it.

I give you Frankenbeam, one idea I am playing with to fix the 4 inch floor problem.
Here is my frame structure with problematic main floor beams highlighted: